Does anyone have Carbon Steel Piping where the header interfaces with the buildings? Do you have corrosion/leak issues with these lines? If yes, what have you done to identify and combat the issue?
Does anyone have Carbon Steel Piping where the header interfaces with the buildings? Do you have corrosion/leak issues with these lines? If yes, what have you done to identify and combat the issue?
Wolf Creek does. We have cathodic protection on these lines and they were originally externally coated with bitomastic. We have not had leaks as of yet.